>So? Assume 50% efficiency in the PSs, so 2x 300 Watt PSs means they consume
That's a real crummy SMPS at 50%! I'd expect more like 65% for a cheapo,
and 70% or better for a quality supply.
>1200 Watts total. At 3000 Watts, you could run for hours (2-3 I guess) - how
>common are multi-hour power outages in your area? Does your need for
>constant uptime justify the expense in batteries?
Unit confusion: 3 kVA != 3kVAh.
For example, the 2kVA Powerware I snagged recently has 4 internal
batteries, each 12V, 9Ah. That's only 432 VAh, or about 5 minutes of
runtime at max load.