[rescue] I'm not an EE Q - clarification
Greg A. Woods
woods at weird.com
Fri Jul 19 00:02:56 CDT 2002
My guess is that it means "no thinner than." Remember AWG numbers get
larger as the wire gets thinner, so the _maximum_ AWG number in this
case is #12.
The question of course can easily be answered by knowing how much
current the machine might draw (i.e. what rating the fuse has -- a
machine can draw as much power as the fuse will pass under failure
conditions!), and then looking up that value in the appropriate
electrical engineering tables.
Here is a portion of a current & AWG table from the Amateur Radio Relay
Handbook, 1985, probably for stranded wire, though I'm not 100% sure.
AWG dia circ open cable ft/lb ohms/
mils mils air A Amp bare 1000'
10 101.9 10380 55 33 31.82 1.018
12 80.8 6530 41 23 50.59 1.619
14 64.1 4107 32 17 80.44 2.575
and here's another table giving recommendations by length of run for
low-voltage power (probably stranded) wire from the rec.audio.car FAQ:
Length of run (in feet)
Current 0-4 4-7 7-10 10-13 13-16 16-19 19-22 22-28
0-20A 14 12 12 10 10 8 8 8
20-35A 12 10 8 8 6 6 6 4
35-50A 10 8 8 6 6 4 4 4
50-65A 8 8 6 4 4 4 4 2
65-85A 6 6 4 4 2 2 2 0
85-105A 6 6 4 2 2 2 2 0
105-125A 4 4 4 2 2 0 0 0
125-150A 2 2 2 2 0 0 0 00
I note that Cisco recommends 12 AWG or even 10 AWG for 20 Amps.....
IIRC 12AWG stranded wire carrying 20 Amps will actually run up to 75F.
(you probably don't want a lot of voltage drop, so 10 AWG will be
guarantee good power if you've got more than 10 feet or so to run)
--
Greg A. Woods
+1 416 218-0098; <g.a.woods at ieee.org>; <woods at robohack.ca>
Planix, Inc. <woods at planix.com>; VE3TCP; Secrets of the Weird <woods at weird.com>
More information about the rescue
mailing list